Hi Guys, Fitting an 8.5Kw (cheapo Triton) shower for a mate`s mate. 15 metre pretty much straight run from consumer unit. Is 6mm cable gonna do or will I have to up it to 10mm. TIA
Back to top
 

TC Holder Maxscan GS500 OBDII code reader/EML resetter available..
 
IP Logged
 
Ziad
Omega Knight
*****
Offline


They say money talks,but
all mine says is Goodbye!

Posts: 1054
Bahrain
Gender: male

Drives: 2000 Opel Omega 3.0 V6 (Sold), 2008 BMW 330i convertible hardtop (totaled), Nissan Armada SE 5.7L V8 & 2011 Mitsubishi Lancer GT
Re: Fitting Electric Shower
Reply #1 - 28. May 2009 at 20:46
 
I'd suggest you go with the 10 mm wiring. I do not trust these thing on a 6 mm. The wires tend to heat a lot when in use IMO on the 6 mm.  Undecided
Back to top
« Last Edit: 28. May 2009 at 20:46 by Ziad »  
Ziad Ziad  
IP Logged
 
Gareth Lewis
Senior Member
****
Offline


eCommerce and Website
Design & Implementation

Posts: 600
Glossop, Derbyshire
Gender: male

Drives: 2000 Omega 2.5 24V Elite Auto
Re: Fitting Electric Shower
Reply #2 - 28. May 2009 at 20:52
 
Would you like me to ask one of the builders who have been here 9 BLOODY DAYS fitting an electric shower in our house!! Angry Angry Angry

Supposed to be a 5 day job to convert shower room to a wet room type and to get the shower off the combi boiler onto its own power and water supply.

I could have done it quicker myself Wink Wink Wink
Back to top
 

Website:
Successful Website Solutions
eCommerce and Website Design, Management & Implementation
WWW Gareth.Lewis  
IP Logged
 
miggcddave
Senior Member
****
Offline



Posts: 690
  south wales
Gender: male

Drives: 97 2ltr cd saloon :kwaka zzr 1100  honda  vf 750
Re: Fitting Electric Shower
Reply #3 - 28. May 2009 at 21:11
 
RobG wrote on 28. May 2009 at 20:38:
Hi Guys, Fitting an 8.5Kw (cheapo Triton) shower for a mate`s mate. 15 metre pretty much straight run from consumer unit. Is 6mm cable gonna do or will I have to up it to 10mm. TIA

do you now the regs on fitting a shower .rcd switch earth cable thickness shower switch with pull cord earth cable on all pipe work ? if you are not sure mate get a spark to fit it if it goes wrong a shower will kill Sad Sad
Back to top
 
 
IP Logged
 
RobG
Omega Lord
*******
Offline


I might have a link, pic
or part number for that

Posts: 7968
Bristol
Gender: male

Drives: 53 plate 2.2 CD auto
Re: Fitting Electric Shower
Reply #4 - 28. May 2009 at 21:16
 
miggcddave wrote on 28. May 2009 at 21:11:
RobG wrote on 28. May 2009 at 20:38:
Hi Guys, Fitting an 8.5Kw (cheapo Triton) shower for a mate`s mate. 15 metre pretty much straight run from consumer unit. Is 6mm cable gonna do or will I have to up it to 10mm. TIA

do you now the regs on fitting a shower .rcd switch earth cable thickness shower switch with pull cord earth cable on all pipe work ? if you are not sure mate get a spark to fit it if it goes wrong a shower will kill Sad Sad

Yeah, I know all that mate, 45A MCB @ consumer unit, 30ma RCCB protecting the circuit and a 45A double pole isolating pull cord/switch. Just wondering whether the 6mm T/E will de-rate due to the cable run. Thumbs Up!
Back to top
 

TC Holder Maxscan GS500 OBDII code reader/EML resetter available..
 
IP Logged
 
miggcddave
Senior Member
****
Offline



Posts: 690
  south wales
Gender: male

Drives: 97 2ltr cd saloon :kwaka zzr 1100  honda  vf 750
Re: Fitting Electric Shower
Reply #5 - 28. May 2009 at 21:21
 
RobG wrote on 28. May 2009 at 21:16:
miggcddave wrote on 28. May 2009 at 21:11:
RobG wrote on 28. May 2009 at 20:38:
Hi Guys, Fitting an 8.5Kw (cheapo Triton) shower for a mate`s mate. 15 metre pretty much straight run from consumer unit. Is 6mm cable gonna do or will I have to up it to 10mm. TIA

do you now the regs on fitting a shower .rcd switch earth cable thickness shower switch with pull cord earth cable on all pipe work ? if you are not sure mate get a spark to fit it if it goes wrong a shower will kill Sad Sad

Yeah, I know all that mate, 45A MCB @ consumer unit, 30ma RCCB protecting the circuit and a 45A double pole isolating pull cord/switch. Just wondering whether the 6mm T/E will de-rate due to the cable run. Thumbs Up!

yea that sounds good to me mate but i would use 10mm T/E just to be on the safe side; and if you up grade your shower in the future you got the cable to take it  good luck mate Thumbs Up!
Back to top
 
 
IP Logged
 
RobG
Omega Lord
*******
Offline


I might have a link, pic
or part number for that

Posts: 7968
Bristol
Gender: male

Drives: 53 plate 2.2 CD auto
Re: Fitting Electric Shower
Reply #6 - 28. May 2009 at 21:23
 
miggcddave wrote on 28. May 2009 at 21:21:
RobG wrote on 28. May 2009 at 21:16:
miggcddave wrote on 28. May 2009 at 21:11:
RobG wrote on 28. May 2009 at 20:38:
Hi Guys, Fitting an 8.5Kw (cheapo Triton) shower for a mate`s mate. 15 metre pretty much straight run from consumer unit. Is 6mm cable gonna do or will I have to up it to 10mm. TIA

do you now the regs on fitting a shower .rcd switch earth cable thickness shower switch with pull cord earth cable on all pipe work ? if you are not sure mate get a spark to fit it if it goes wrong a shower will kill Sad Sad

Yeah, I know all that mate, 45A MCB @ consumer unit, 30ma RCCB protecting the circuit and a 45A double pole isolating pull cord/switch. Just wondering whether the 6mm T/E will de-rate due to the cable run. Thumbs Up!

yea that sounds good to me mate but i would use 10mm T/E just to be on the safe side; and if you up grade your shower in the future you got the cable to take it  good luck mate Thumbs Up!

Thought about that. 10mm it`s gonna be (bloody dear though), ah well, what price safety & peace of mind Thumbs Up!
Back to top
 

TC Holder Maxscan GS500 OBDII code reader/EML resetter available..
 
IP Logged
 
miggcddave
Senior Member
****
Offline



Posts: 690
  south wales
Gender: male

Drives: 97 2ltr cd saloon :kwaka zzr 1100  honda  vf 750
Re: Fitting Electric Shower
Reply #7 - 28. May 2009 at 21:27
 
RobG wrote on 28. May 2009 at 21:23:
miggcddave wrote on 28. May 2009 at 21:21:
RobG wrote on 28. May 2009 at 21:16:
miggcddave wrote on 28. May 2009 at 21:11:
RobG wrote on 28. May 2009 at 20:38:
Hi Guys, Fitting an 8.5Kw (cheapo Triton) shower for a mate`s mate. 15 metre pretty much straight run from consumer unit. Is 6mm cable gonna do or will I have to up it to 10mm. TIA

do you now the regs on fitting a shower .rcd switch earth cable thickness shower switch with pull cord earth cable on all pipe work ? if you are not sure mate get a spark to fit it if it goes wrong a shower will kill Sad Sad

Yeah, I know all that mate, 45A MCB @ consumer unit, 30ma RCCB protecting the circuit and a 45A double pole isolating pull cord/switch. Just wondering whether the 6mm T/E will de-rate due to the cable run. Thumbs Up!

yea that sounds good to me mate but i would use 10mm T/E just to be on the safe side; and if you up grade your shower in the future you got the cable to take it  good luck mate Thumbs Up!

Thought about that. 10mm it`s gonna be (bloody dear though), ah well, what price safety & peace of mind Thumbs Up!

have you had a look at screw fix direct good prices in that book ; worth a look its on line  Thumbs Up!
Back to top
 
 
IP Logged
 
RobG
Omega Lord
*******
Offline


I might have a link, pic
or part number for that

Posts: 7968
Bristol
Gender: male

Drives: 53 plate 2.2 CD auto
Re: Fitting Electric Shower
Reply #8 - 28. May 2009 at 21:34
 
miggcddave wrote on 28. May 2009 at 21:27:
RobG wrote on 28. May 2009 at 21:23:
miggcddave wrote on 28. May 2009 at 21:21:
RobG wrote on 28. May 2009 at 21:16:
miggcddave wrote on 28. May 2009 at 21:11:
RobG wrote on 28. May 2009 at 20:38:
Hi Guys, Fitting an 8.5Kw (cheapo Triton) shower for a mate`s mate. 15 metre pretty much straight run from consumer unit. Is 6mm cable gonna do or will I have to up it to 10mm. TIA

do you now the regs on fitting a shower .rcd switch earth cable thickness shower switch with pull cord earth cable on all pipe work ? if you are not sure mate get a spark to fit it if it goes wrong a shower will kill Sad Sad

Yeah, I know all that mate, 45A MCB @ consumer unit, 30ma RCCB protecting the circuit and a 45A double pole isolating pull cord/switch. Just wondering whether the 6mm T/E will de-rate due to the cable run. Thumbs Up!

yea that sounds good to me mate but i would use 10mm T/E just to be on the safe side; and if you up grade your shower in the future you got the cable to take it  good luck mate Thumbs Up!

Thought about that. 10mm it`s gonna be (bloody dear though), ah well, what price safety & peace of mind Thumbs Up!

have you had a look at screw fix direct good prices in that book ; worth a look its on line  Thumbs Up!

I`ll have a gander. Usually get most of my stuff from "Toolstation" Smiley
Back to top
 

TC Holder Maxscan GS500 OBDII code reader/EML resetter available..
 
IP Logged
 
miggcddave
Senior Member
****
Offline



Posts: 690
  south wales
Gender: male

Drives: 97 2ltr cd saloon :kwaka zzr 1100  honda  vf 750
Re: Fitting Electric Shower
Reply #9 - 28. May 2009 at 21:46
 
25 mtr reel for £48 10mm t/e in screw fix with vat Undecided
Back to top
 
 
IP Logged
 
RobG
Omega Lord
*******
Offline


I might have a link, pic
or part number for that

Posts: 7968
Bristol
Gender: male

Drives: 53 plate 2.2 CD auto
Re: Fitting Electric Shower
Reply #10 - 28. May 2009 at 21:47
 
miggcddave wrote on 28. May 2009 at 21:46:
25 mtr reel for £48 10mm t/e in screw fix with vat Undecided

Same bloody price @ the Toolstation Cry Cry
Back to top
 

TC Holder Maxscan GS500 OBDII code reader/EML resetter available..
 
IP Logged
 
miggcddave
Senior Member
****
Offline



Posts: 690
  south wales
Gender: male

Drives: 97 2ltr cd saloon :kwaka zzr 1100  honda  vf 750
Re: Fitting Electric Shower
Reply #11 - 28. May 2009 at 21:50
 
RobG wrote on 28. May 2009 at 21:47:
miggcddave wrote on 28. May 2009 at 21:46:
25 mtr reel for £48 10mm t/e in screw fix with vat Undecided

Same bloody price @ the Toolstation Cry Cry

oh well ? but like you siad safety first
Back to top
 
 
IP Logged
 
KillerWatt
Ex Member


Re: Fitting Electric Shower
Reply #12 - 28. May 2009 at 23:10
 
RobG wrote on 28. May 2009 at 21:16:
Yeah, I know all that mate, 45A MCB @ consumer unit, 30ma RCCB protecting the circuit and a 45A double pole isolating pull cord/switch. Just wondering whether the 6mm T/E will de-rate due to the cable run. Thumbs Up!

That's double pole isolator with indication, and you need to be Part P for anything concerning a bathroom.

It's more than just cable length versus current drain when carrying out an installation.

Seriously, get a qualified sparks in.....because a mistake can see you in the dock for manslaughter if something tragic occurs.
Back to top
 
 
IP Logged
 
Zulu77
Ex Member


Re: Fitting Electric Shower
Reply #13 - 28. May 2009 at 23:13
 
Quote:
RobG wrote on 28. May 2009 at 21:16:
Yeah, I know all that mate, 45A MCB @ consumer unit, 30ma RCCB protecting the circuit and a 45A double pole isolating pull cord/switch. Just wondering whether the 6mm T/E will de-rate due to the cable run. Thumbs Up!

That's double pole isolator with indication, and you need to be Part P for anything concerning a bathroom.

It's more than just cable length versus current drain when carrying out an installation.

Seriously, get a qualified sparks in.....because a mistake can see you in the dock for manslaughter if something tragic occurs.



Wise words Killer Thumbs Up! Thumbs Up!
Back to top
 
 
IP Logged
 
miggcddave
Senior Member
****
Offline



Posts: 690
  south wales
Gender: male

Drives: 97 2ltr cd saloon :kwaka zzr 1100  honda  vf 750
Re: Fitting Electric Shower
Reply #14 - 28. May 2009 at 23:13
 
Quote:
RobG wrote on 28. May 2009 at 21:16:
Yeah, I know all that mate, 45A MCB @ consumer unit, 30ma RCCB protecting the circuit and a 45A double pole isolating pull cord/switch. Just wondering whether the 6mm T/E will de-rate due to the cable run. Thumbs Up!

That's double pole isolator with indication, and you need to be Part P for anything concerning a bathroom.

It's more than just cable length versus current drain when carrying out an installation.

Seriously, get a qualified sparks in.....because a mistake can see you in the dock for manslaughter if something tragic occurs.

well siad K W thats the words i was looking for  Thumbs Up!