Any combi boiler experts out there? (Read 1661 times)
Nickbat
Omega Lord
*******
Offline



Posts: 7167
London NW7
Gender: male

Drives: 2002 2.6CD Auto
Any combi boiler experts out there?
15. Nov 2009 at 15:34
 
I have a problem getting my boiler to kick in when the hot taps are turned on. To get the hot to flow in the kitchen, I have first to turn on the bathroom hot tap, then turn it off once the boiler fires up. However, sometimes, even after turning on the bathroom tap it can take a good minute or two before the boiler fires.

I changed the kitchen taps a couple of weeks ago and the problem, which I think existed before, has become much worse since.

On the boiler (a Vokera Maxin 24), there is a hot water temperature control (just a knob, with a thinner to thicker line denoting min to max) and that is truned to its maximum.

There, that's all the info I can think of.

Is this a situation which requires a service engineer?

Hope not, they cost a fortune!  Sad Cry
Back to top
 

I don't care to belong to a club that accepts people like me as members.
Groucho Marx
 
IP Logged
 
MickAP
Omega Knight
*****
Offline


Facelift 2.5TD Estate
"Chipped" not anymore

Posts: 1592
South Derbyshire
Gender: male

Drives: Facelift TD estate but soon to be a 1.9 ???
Re: Any combi boiler experts out there?
Reply #1 - 15. Nov 2009 at 15:56
 
Does the heating side of things work ok, is it presurrised ok?
Went out to my sons house the other night and his had lost all pressure in the system preventing it from firing up, got it back up to pressure and let loads of air out from the system (heating) and all was ok again, it fired up.

Mick
Back to top
 
 
IP Logged
 
Nickbat
Omega Lord
*******
Offline



Posts: 7167
London NW7
Gender: male

Drives: 2002 2.6CD Auto
Re: Any combi boiler experts out there?
Reply #2 - 15. Nov 2009 at 16:24
 
MickAP wrote on 15. Nov 2009 at 15:56:
Does the heating side of things work ok, is it presurrised ok?
Went out to my sons house the other night and his had lost all pressure in the system preventing it from firing up, got it back up to pressure and let loads of air out from the system (heating) and all was ok again, it fired up.

Mick


Yep, all pressurised and the heating works.
Back to top
 

I don't care to belong to a club that accepts people like me as members.
Groucho Marx
 
IP Logged
 
cem
Omega King
********
Offline



Posts: 13920
Ankara/Turkey
Gender: male

Drives: 97 2.5 V6 Manual CD- Clio Sport
Re: Any combi boiler experts out there?
Reply #3 - 15. Nov 2009 at 16:48
 
problem seems similiar to mine I had before..

there is a valve/gasket similiar that must be changed..

cheap not something expensive in mine.. I think it will be same for yours..by the way I call someone and watch when he's changing Grin Thumbs Up!
Back to top
 
cem  
IP Logged
 
Debs.
Omega Lord
*******
Offline


A denizen of The Wirral
peninsula

Posts: 7386
Gender: female

Drives: 2.5 V6 CDX Estate (1999)
Re: Any combi boiler experts out there?
Reply #4 - 15. Nov 2009 at 16:53
 
My thoughts...
London hard water: heat exchanger choked or flow sensor/diaphragm is sticky or faulty. Wink
Back to top
 
 
IP Logged
 
cem
Omega King
********
Offline



Posts: 13920
Ankara/Turkey
Gender: male

Drives: 97 2.5 V6 Manual CD- Clio Sport
Re: Any combi boiler experts out there?
Reply #5 - 15. Nov 2009 at 16:55
 
Debs. wrote on 15. Nov 2009 at 16:53:
My thoughts...
London hard water: heat exchanger choked or flow sensor/diaphragm is sticky or faulty. Wink


long live Debs Thumbs Up!
Back to top
 
cem  
IP Logged
 
Marks DTM Calib
Administrator
****************
Offline


Ex Member

Posts: 25671
Northern Hemisphere
Gender: male

Drives: Astra J, Mum Bus, Dexta Tractor, 108 DMU wip
Re: Any combi boiler experts out there?
Reply #6 - 15. Nov 2009 at 17:28
 
Flow sensor......I would say
Back to top
 
Marks DTM Calib  
IP Logged
 
PhilRich
Omega Lord
*******
Offline


Proud to be English, with
no apologies to ANYONE!

Posts: 6825
NorthEast Coast
Gender: male

Drives: 2002 2.2CDX 4dr Auto. LPG Converted.
Re: Any combi boiler experts out there?
Reply #7 - 15. Nov 2009 at 18:16
 
Debs. wrote on 15. Nov 2009 at 16:53:
My thoughts...
London hard water: heat exchanger choked or flow sensor/diaphragm is sticky or faulty. Wink



Spot on Debs, you clever girl! I'm a retired gas service engineer and those are the two most likely culprits Thumbs Up!
Back to top
 

Apparently the Skipper said "Hard a Port!" but I went to Starboard, 'cos i'm Hard a Hearin'!
...
 
IP Logged
 
Nickbat
Omega Lord
*******
Offline



Posts: 7167
London NW7
Gender: male

Drives: 2002 2.6CD Auto
Re: Any combi boiler experts out there?
Reply #8 - 15. Nov 2009 at 22:12
 
PhilRich wrote on 15. Nov 2009 at 18:16:
Debs. wrote on 15. Nov 2009 at 16:53:
My thoughts...
London hard water: heat exchanger choked or flow sensor/diaphragm is sticky or faulty. Wink



Spot on Debs, you clever girl! I'm a retired gas service engineer and those are the two most likely culprits Thumbs Up!


Thanks girls and guys!  Wink

I guess that's an engineer job, then. Sad

Especially as I've heard it's illegal to fiddle with them if you're not Corgi registered.
Back to top
 

I don't care to belong to a club that accepts people like me as members.
Groucho Marx
 
IP Logged
 
ENFIELD_MV6
Senior Member
****
Offline


previously from leicestershire

Posts: 526
Enfield
Gender: male

Drives: MV6 Estate Auto, Megane Scenic 1.4 16v
Re: Any combi boiler experts out there?
Reply #9 - 15. Nov 2009 at 23:23
 
Nickbat wrote on 15. Nov 2009 at 22:12:
PhilRich wrote on 15. Nov 2009 at 18:16:
Debs. wrote on 15. Nov 2009 at 16:53:
My thoughts...
London hard water: heat exchanger choked or flow sensor/diaphragm is sticky or faulty. Wink



Spot on Debs, you clever girl! I'm a retired gas service engineer and those are the two most likely culprits Thumbs Up!


Thanks girls and guys!  Wink

I guess that's an engineer job, then. Sad

Especially as I've heard it's illegal to fiddle with them if you're not Corgi registered.


if the person who comes is CORGI registered avoid as it means that they have not took the gas safe exam which has superceeded corgi. Basically corgi no longer exists so if thats the only badge/crudentials they have ask them if they are gas safe registered  Thumbs Up! Thumbs Up! Thumbs Up!
Back to top
 
 
IP Logged
 
Nickbat
Omega Lord
*******
Offline



Posts: 7167
London NW7
Gender: male

Drives: 2002 2.6CD Auto
Re: Any combi boiler experts out there?
Reply #10 - 15. Nov 2009 at 23:25
 
ENFIELD_MV6 wrote on 15. Nov 2009 at 23:23:
Nickbat wrote on 15. Nov 2009 at 22:12:
PhilRich wrote on 15. Nov 2009 at 18:16:
Debs. wrote on 15. Nov 2009 at 16:53:
My thoughts...
London hard water: heat exchanger choked or flow sensor/diaphragm is sticky or faulty. Wink



Spot on Debs, you clever girl! I'm a retired gas service engineer and those are the two most likely culprits Thumbs Up!


Thanks girls and guys!  Wink

I guess that's an engineer job, then. Sad

Especially as I've heard it's illegal to fiddle with them if you're not Corgi registered.


if the person who comes is CORGI registered avoid as it means that they have not took the gas safe exam which has superceeded corgi. Basically corgi no longer exists so if thats the only badge/crudentials they have ask them if they are gas safe registered  Thumbs Up! Thumbs Up! Thumbs Up!


Thanks for the tip!  Thumbs Up!
Back to top
 

I don't care to belong to a club that accepts people like me as members.
Groucho Marx
 
IP Logged
 
ENFIELD_MV6
Senior Member
****
Offline


previously from leicestershire

Posts: 526
Enfield
Gender: male

Drives: MV6 Estate Auto, Megane Scenic 1.4 16v
Re: Any combi boiler experts out there?
Reply #11 - 15. Nov 2009 at 23:29
 
Nickbat wrote on 15. Nov 2009 at 23:25:
ENFIELD_MV6 wrote on 15. Nov 2009 at 23:23:
Nickbat wrote on 15. Nov 2009 at 22:12:
PhilRich wrote on 15. Nov 2009 at 18:16:
Debs. wrote on 15. Nov 2009 at 16:53:
My thoughts...
London hard water: heat exchanger choked or flow sensor/diaphragm is sticky or faulty. Wink



Spot on Debs, you clever girl! I'm a retired gas service engineer and those are the two most likely culprits Thumbs Up!


Thanks girls and guys!  Wink

I guess that's an engineer job, then. Sad

Especially as I've heard it's illegal to fiddle with them if you're not Corgi registered.


if the person who comes is CORGI registered avoid as it means that they have not took the gas safe exam which has superceeded corgi. Basically corgi no longer exists so if thats the only badge/crudentials they have ask them if they are gas safe registered  Thumbs Up! Thumbs Up! Thumbs Up!


Thanks for the tip!  Thumbs Up!


No worries use to help a gas safe engineer do some plumbing work (fetching and carrying plus lifting the boiler onto its brackets lol) and learnt a fair bit as he only ever fitted combi boilers when replacing systems so did learn a fair bit along the way
Back to top
 
 
IP Logged
 
Marks DTM Calib
Administrator
****************
Offline


Ex Member

Posts: 25671
Northern Hemisphere
Gender: male

Drives: Astra J, Mum Bus, Dexta Tractor, 108 DMU wip
Re: Any combi boiler experts out there?
Reply #12 - 16. Nov 2009 at 08:30
 
Nickbat wrote on 15. Nov 2009 at 22:12:
PhilRich wrote on 15. Nov 2009 at 18:16:
Debs. wrote on 15. Nov 2009 at 16:53:
My thoughts...
London hard water: heat exchanger choked or flow sensor/diaphragm is sticky or faulty. Wink



Spot on Debs, you clever girl! I'm a retired gas service engineer and those are the two most likely culprits Thumbs Up!


Thanks girls and guys!  Wink

I guess that's an engineer job, then. Sad

Especially as I've heard it's illegal to fiddle with them if you're not Corgi registered.


Not that any of them are engineers, fitters or technicians is the correct reference.

Also, the laws are quite clear as they dont state that you need any specific certification if doing a job for no reward, you simply need to prove compitence (for which thier are methods).

To add to it, the chances are that the flow sensor is external to the main gas part (combustion chamber and burner section) and hence is very accessable with pretty much 0 risk on the gas front (and hence means the job technicaly falls outside that covered by the gas regs anyway).

Even better, the manual for the lump will probably tell you where it is and the part number.

I dont buy the heat exchanger bit as this would not slow the boiler firing unless the flow rate was stupidly restricted.

I get bits here:

http://www.onlineboilerspares.com/
Back to top
« Last Edit: 16. Nov 2009 at 08:50 by Marks DTM Calib »  
Marks DTM Calib  
IP Logged
 
Marks DTM Calib
Administrator
****************
Offline


Ex Member

Posts: 25671
Northern Hemisphere
Gender: male

Drives: Astra J, Mum Bus, Dexta Tractor, 108 DMU wip
Re: Any combi boiler experts out there?
Reply #13 - 16. Nov 2009 at 08:32
 
In fact, here is the diagram in question

http://www.onlineboilerspares.com/product1897.html
Back to top
 
Marks DTM Calib  
IP Logged
 
Marks DTM Calib
Administrator
****************
Offline


Ex Member

Posts: 25671
Northern Hemisphere
Gender: male

Drives: Astra J, Mum Bus, Dexta Tractor, 108 DMU wip
Re: Any combi boiler experts out there?
Reply #14 - 16. Nov 2009 at 08:41
 
And here is the manual

http://vokera.excaliburstudio.co.uk/wp-content/uploads/2009/04/maxin_24e_28e_ins...

Note, the manaul confirms that you do not have to access the burner chamber.
Back to top
 