Boiler Clocks (Read 2135 times)
davethediver
Omega Knight
*****
Offline



Posts: 1323
Blackburn, Lancs.
Gender: male

Drives: 2.2 CD Facelift (2001)
Boiler Clocks
02. Feb 2011 at 22:58
 
Does a combi bolier need to have a room thermostat or can it run off just a time clock?
Back to top
 

“It is not necessary to understand things in order to argue about them.”
P.A. Caron de Beaumarchais
 
IP Logged
 
Vamps
Omega King
********
Offline


Flying Tonight, so Be
Prepared.

Posts: 16571
Bishop Middleham, Co Durham.
Gender: male

Drives: 2.0L Auto Estate & 2.2 CD Auto Saloon
Re: Boiler Clocks
Reply #1 - 02. Feb 2011 at 23:17
 
davethediver wrote on 02. Feb 2011 at 22:58:
Does a combi bolier need to have a room thermostat or can it run off just a time clock?


I am not sure about the question, yes it will have a time clock, but surly also a thermostat...what are you trying to do, if you only want to control the heating by a time clock just turn the stat up high and set the clock.....
Undecided Roll Eyes
Back to top
 

IMG]http://i275.photobucket.com/albums/jj284/floodm_photos/DSCF1767.jpg[/IMG]
Vamps flood748  
IP Logged
 
Nickbat
Omega Lord
*******
Offline



Posts: 7167
London NW7
Gender: male

Drives: 2002 2.6CD Auto
Re: Boiler Clocks
Reply #2 - 02. Feb 2011 at 23:18
 
davethediver wrote on 02. Feb 2011 at 22:58:
Does a combi bolier need to have a room thermostat or can it run off just a time clock?


My combi has a thermostat near the stairwell. Individual rooms are then controlled by the rad valves.
Back to top
 

I don't care to belong to a club that accepts people like me as members.
Groucho Marx
 
IP Logged
 
davethediver
Omega Knight
*****
Offline



Posts: 1323
Blackburn, Lancs.
Gender: male

Drives: 2.2 CD Facelift (2001)
Re: Boiler Clocks
Reply #3 - 02. Feb 2011 at 23:24
 
The boiler did have an integral mechanical clock which broke Sad there is no house stat but all the rads do have TRV's on. I have attempted to wire in a new single chanel honeywell timeclock and all though it has power to the timer i can't get it to operate the heating Angry

I'm not a sparky so its a bit of trial and error or help off OOF Grin Grin it did work without a housestat just don't know what im doing wrong with this timer Embarrassed Embarrassed
Back to top
 

“It is not necessary to understand things in order to argue about them.”
P.A. Caron de Beaumarchais
 
IP Logged
 
Kevin Wood
Global Moderator
Admin Team
*******
Offline



Posts: 20377
Alton, Hampshire
Gender: male

Drives: 3.2 MV6 (LPG), Westfield
Re: Boiler Clocks
Reply #4 - 03. Feb 2011 at 00:10
 
I believe current regs state that there should be a thermostat in one room in addition to TRVs in all others to prevent the boiler working when no heat is called for.

As to why it doesn't work, it would depend on the specific boiler so try and find the installation manual (should be left with the installation). Failing that download one from the web.

Normally there will be provision for either a mains power input from a timeswitch plus room thermostat or a set of contacts which close when the CH is calling for heat.

Kevin
Back to top
 

Tech2 services currently available. See TheBoy's price list: http://theboy.omegaowners.com/
 
IP Logged
 
Kevin Wood
Global Moderator
Admin Team
*******
Offline



Posts: 20377
Alton, Hampshire
Gender: male

Drives: 3.2 MV6 (LPG), Westfield
Re: Boiler Clocks
Reply #5 - 03. Feb 2011 at 00:12
 
Ahh- if the boiler has an internal timeswitch which is broken can you be sure it's calling for heat or has it failed in the "off" position? Does the boiler fire up if you select constant CH?

Might be easier to source a replacement timeswitch module for the boiler, TBH.

Kevin
Back to top
 

Tech2 services currently available. See TheBoy's price list: http://theboy.omegaowners.com/
 
IP Logged
 
davethediver
Omega Knight
*****
Offline



Posts: 1323
Blackburn, Lancs.
Gender: male

Drives: 2.2 CD Facelift (2001)
Re: Boiler Clocks
Reply #6 - 03. Feb 2011 at 00:31
 
Kevin Wood wrote on 03. Feb 2011 at 00:12:
Ahh- if the boiler has an internal timeswitch which is broken can you be sure it's calling for heat or has it failed in the "off" position? Does the boiler fire up if you select constant CH?

Might be easier to source a replacement timeswitch module for the boiler, TBH.

Kevin


The boiler does fire up if the timed/constant switch is placed on constant. I,m pretty certain its something to do with the switched live connection as said electrics ain't my stong point.

Part L of the building regs does state that a CH system should have a temperature contol as well as a time control and that bedroom rads have TRV's on them.

Going to look a bit of a tool at work if i have to ask one of the engineers (work for a large domestic heating firm) Embarrassed Embarrassed
Back to top
 

“It is not necessary to understand things in order to argue about them.”
P.A. Caron de Beaumarchais
 
IP Logged
 
PhilRich
Omega Lord
*******
Offline


Proud to be English, with
no apologies to ANYONE!

Posts: 6825
NorthEast Coast
Gender: male

Drives: 2002 2.2CDX 4dr Auto. LPG Converted.
Re: Boiler Clocks
Reply #7 - 03. Feb 2011 at 07:45
 
davethediver wrote on 03. Feb 2011 at 00:31:
Kevin Wood wrote on 03. Feb 2011 at 00:12:
Ahh- if the boiler has an internal timeswitch which is broken can you be sure it's calling for heat or has it failed in the "off" position? Does the boiler fire up if you select constant CH?

Might be easier to source a replacement timeswitch module for the boiler, TBH.Kevin


The boiler does fire up if the timed/constant switch is placed on constant. I,m pretty certain its something to do with the switched live connection as said electrics ain't my stong point.

Part L of the building regs does state that a CH system should have a temperature contol as well as a time control and that bedroom rads have TRV's on them.

Going to look a bit of a tool at work if i have to ask one of the engineers (work for a large domestic heating firm) Embarrassed Embarrassed






Then you couldn't be in a better place to obtain a replacement surely, & at 'cost'? Thumbs Up!
Back to top
 

Apparently the Skipper said "Hard a Port!" but I went to Starboard, 'cos i'm Hard a Hearin'!
...
 
IP Logged
 
Kevin Wood
Global Moderator
Admin Team
*******
Offline



Posts: 20377
Alton, Hampshire
Gender: male

Drives: 3.2 MV6 (LPG), Westfield
Re: Boiler Clocks
Reply #8 - 03. Feb 2011 at 09:27
 
PhilRich wrote on 03. Feb 2011 at 07:45:
davethediver wrote on 03. Feb 2011 at 00:31:
Kevin Wood wrote on 03. Feb 2011 at 00:12:
Ahh- if the boiler has an internal timeswitch which is broken can you be sure it's calling for heat or has it failed in the "off" position? Does the boiler fire up if you select constant CH?

Might be easier to source a replacement timeswitch module for the boiler, TBH.Kevin


The boiler does fire up if the timed/constant switch is placed on constant. I,m pretty certain its something to do with the switched live connection as said electrics ain't my stong point.

Part L of the building regs does state that a CH system should have a temperature contol as well as a time control and that bedroom rads have TRV's on them.

Going to look a bit of a tool at work if i have to ask one of the engineers (work for a large domestic heating firm) Embarrassed Embarrassed






Then you couldn't be in a better place to obtain a replacement surely, & at 'cost'? Thumbs Up!


Yep, and a manual. What model of boiler is it? Worth looking for documentation online?

Kevin
Back to top
 

Tech2 services currently available. See TheBoy's price list: http://theboy.omegaowners.com/
 
IP Logged
 
Marks DTM Calib
Administrator
****************
Offline


Ex Member

Posts: 25671
Northern Hemisphere
Gender: male

Drives: Astra J, Mum Bus, Dexta Tractor, 108 DMU wip
Re: Boiler Clocks
Reply #9 - 03. Feb 2011 at 10:30
 
You will be hard pushed to find a real engineer in a domestic heating firm  Thumbs Up! Grin

Post up the boiler make and model and we will see what we can do
Back to top
 
Marks DTM Calib  
IP Logged
 
davethediver
Omega Knight
*****
Offline



Posts: 1323
Blackburn, Lancs.
Gender: male

Drives: 2.2 CD Facelift (2001)
Re: Boiler Clocks
Reply #10 - 03. Feb 2011 at 12:32
 
Boiler is an old Potterton Lynx 2 and time clock is a simple 1 day 1 channel honeywell unit.

And Mark you are of course right the only one i'd class as a real engineer (40yrs in the trade and a very knowlegable guy on most things) is on sodding holiday and i don't want any of the others coming round to 'fix it' for me because thats One point to them and None to me Grin Grin
Back to top
 

“It is not necessary to understand things in order to argue about them.”
P.A. Caron de Beaumarchais
 
IP Logged
 
Marks DTM Calib
Administrator
****************
Offline


Ex Member

Posts: 25671
Northern Hemisphere
Gender: male

Drives: Astra J, Mum Bus, Dexta Tractor, 108 DMU wip
Re: Boiler Clocks
Reply #11 - 03. Feb 2011 at 13:09
 
davethediver wrote on 03. Feb 2011 at 12:32:
Boiler is an old Potterton Lynx 2 and time clock is a simple 1 day 1 channel honeywell unit.

And Mark you are of course right the only one i'd class as a real engineer (40yrs in the trade and a very knowlegable guy on most things) is on sodding holiday and i don't want any of the others coming round to 'fix it' for me because thats One point to them and None to me Grin Grin


The engineer designed the boiler, technicians repair them and fitters install them....  Grin

Heres the installation manual:

http://www.partsarena.co.uk/baxi/System/DATA/Dx/DS1/installation/2511/I19-2511/I...

It shows how the timer needs to be wired (dead easy to do)
Back to top
 
Marks DTM Calib  
IP Logged
 
Marks DTM Calib
Administrator
****************
Offline


Ex Member

Posts: 25671
Northern Hemisphere
Gender: male

Drives: Astra J, Mum Bus, Dexta Tractor, 108 DMU wip
Re: Boiler Clocks
Reply #12 - 03. Feb 2011 at 13:10
 
What timer are you fitting and I will do a quick connection list for you.
Back to top
 
Marks DTM Calib  
IP Logged
 
Lioned
Junior Member
**
Offline



Posts: 238
South East London
Gender: male

Drives: Omega estate 2.2ltr 53 reg
Re: Boiler Clocks
Reply #13 - 03. Feb 2011 at 17:36
 
For combi boiler use a programmable room stat.Quite simple to fit just a single 'channel' 2 wires,basically acts like a switch.

Just fitted one for my son Honeywell cm907,cost me about  60 quid there are cheaper ones.

Just look up your boiler instructions to get the right connections.

Just looked at the wiring diagram and you would use terminals 3 and 4 and remove the link.The honeywell stat does not require a permanent live or neutral as it is battery operated.
Back to top
« Last Edit: 03. Feb 2011 at 17:49 by Lioned »  
 
IP Logged
 
davethediver
Omega Knight
*****
Offline



Posts: 1323
Blackburn, Lancs.
Gender: male

Drives: 2.2 CD Facelift (2001)
Re: Boiler Clocks
Reply #14 - 03. Feb 2011 at 22:02
 
Marks DTM Calib wrote on 03. Feb 2011 at 13:10:
What timer are you fitting and I will do a quick connection list for you.


Its a Honeywell ST9100a.

TIA Dave